So based on the code -
The first requirement is that the current temp be less than the target temp being set by twice the watch increase value. The UM1 firmware comes with a increase vale of 10. So that means if the hotend is at say 180 and you set the new temp to be anything less than or equal to 200, the watch code won't be trigger.
The second requirement is that when the watch temp period elapses (the period by default in the UM1 firmware is 40 seconds), the temp must be ANY AMOUNT greater/equal to than the set temp plus the watch temp increase (10 for the UM1 firmware).
The third key point is that when the second requirement is met, the watch is DISABLE.
So for the UM1, this check won't help if
- The sensor reporting fails in a mode where the reported temp is a high value (10 more than the temp value set) or max value...
- If the sensor reporting fails in any mode after 40 seconds, the error won't be caught.
Obviously, this could and should be improved -
- There shouldn't be a check when the temp is changed that the hotend is less than the set point less twice the watch temp. If the set temp is changed, the watch temp should just be updated along with the watch temp check time to be the current time plus the watch temp time period.
- When the watch temp time period elapses, the temp should be checked to see if it is in the range of set temp plus/minus the watch temp increase. Hmmmm... well, see notes below.
- When the check is done, the check shouldn't be disabled. Instead, it should be set to the current time plus the watch temp period.
Note: After thinking about this a little - obviously, cooling down is a lot slower than heating. So the values might not work well and there might be need for a second set of cold down values used when the set temp is set below the current temp. However, an additional check should be implemented that when the cool down mode values are in effect, the temp should be checked at the heating check period to ensure that it hasn't INCREASED above the temp at the time of the temp change was requested plus the temp increase check value.
Not impossible to code. However, it's quite possible I haven't considered everything and could introduce all sorts if false "heating failed" problems...
Don't have time now but might attempt to implement if someone else (cough GR5 cough Daid cough illuminarti cough) doesn't....
Here is the existing code for the UM1 -
Marlin does this when you change the temp.
void setWatch()
{
#ifdef WATCH_TEMP_PERIOD
for (int e = 0; e < EXTRUDERS; e++)
{
if(degHotend(e) < degTargetHotend(e) - (WATCH_TEMP_INCREASE * 2))
{
watch_start_temp[e] = degHotend(e);
watchmillis[e] = millis();
}
}
#endif
}
Then during heating it does this check during the manage heater routine.
#ifdef WATCH_TEMP_PERIOD
if(watchmillis[e] && millis() - watchmillis[e] > WATCH_TEMP_PERIOD)
{
if(degHotend(e) < watch_start_temp[e] + WATCH_TEMP_INCREASE)
{
setTargetHotend(0, e);
LCD_MESSAGEPGM("Heating failed");
SERIAL_ECHO_START;
SERIAL_ECHOLN("Heating failed");
}else{
watchmillis[e] = 0;
}
}
#endif
For the UM1 version, the values involved
//// Heating sanity check:
// This waits for the watch period in milliseconds whenever an M104 or M109 increases the target temperature
// If the temperature has not increased at the end of that period, the target temperature is set to zero.
// It can be reset with another M104/M109. This check is also only triggered if the target temperature and the current temperature
// differ by at least 2x WATCH_TEMP_INCREASE
#define WATCH_TEMP_PERIOD 40000 //40 seconds
#define WATCH_TEMP_INCREASE 10 //Heat up at least 10 degree in 20 seconds
Recommended Posts
gr5 2,265
Usually "disconnection" means "electrical disconnection". But are you talking about physical disconnection in both cases? So that the sensor was reading room temperature?
Supposedly Marlin tests for this error but obviously it doesn't do a good job. I suspect this error is only caught maybe if the sensor falls out during the heating up step. I suspect once the nozzle is up to temperature, if the sensor falls out, it gets much harder to distinguish the problem using software.
Link to post